[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

incinerators' pollution control equipment



An incinerator manufacturer (?) describes the pollutants to be controlled
from a medwaste incinerator.


>From Pollution Online:
http://www2.pollutiononline.com/content/news/article.asp?DocID={749429EB-525
4-11D3-9A5E-00A0C9C83AFB}&Bucket=HomeFeaturedArticles&VNETCOOKIE=NO


Air-pollution-control Methods--Part 1: Waste-burning Basics
                           8/17/99  This--the first of a
multi-part--presentation introduces some concepts
                           basic to understanding the devices used for
controlling emissions from
                           medical-waste incinerators. 

                                                   By: Isaac Ray

                           The medical-incinerator control-system designer
must comply with existing
                           air-pollution-control requirements, limit
nuisance emissions, and grasp that even
                           an occasional emission-control failure will
probably engender severe public and
                           regulatory reaction. 

                           Also the designer must be mindful that many
non-regulated components should
                           be removed from the incinerator's combustion
stream to safeguard downstream
                           equipment from excessive erosion (physical wear)
and/or corrosion (chemical
                           degradation). 

                           Fortunately, excellent technology exists for the
consistent removal of large,
                           small, and extremely fine particles and acid
gases from discharge gas streams. 

                           Incineration has been the major technology for
disposing of hospital and
                           infectious waste for more than 10 years. 

                           The incineration equipment for this application
normally is small, in a range of 250
                           to 3000-lb/hr capacity, and operated in a batch
mode. An example is a
                           microprocessor-controlled, air fixed-hearth,
two-chamber, prepackaged unit. 

                           Regulatory agencies tend to classify
pathological waste, infectious waste, and
                           medical laboratory waste together under the
general heading of hospital waste.
                           These wastes, however, have different properties
(see Table 1) and require
                           different combustion conditions for optimum
oxidation. 

                           The type of waste produced depends on the nature
of medicine that is practiced
                           at the hospital, the extent to which lab work is
done, the number of beds, the
                           presence of special (such as radioisotope)
facilities, and the hospital's philosophy
                           about what goes to the incinerator. 

                           Trends 

                           In general, the plastic content of hospital
waste continues to grow, from 10% to
                           more than 30% during the last 20 years. Many of
the plastics contain chlorine
                           and generate hydrogen chloride emissions during
incineration. 

                           In addition, most hospitals tend to route more
and more and their waste to the
                           incinerator and less to municipal
solid-waste-disposal facilities. As a result, the
                           paper content of the waste today is greater than
that in Table 1, which reflects
                           conditions prior to hospitals' installing their
incinerators. 

                                                     Table 1
                                             Hospital Waste Composition

                                    Component
                                              Higher
                                              Heating
                                              Value on
                                             Dry Basis,
                                             103Btu/lb
                                                      Bulk
                                                     Density
                                                     as Fired,
                                                      lb/cu ft
                                                            Moisture
                                                             Wt, %
                                                                    Heating
Value
                                                                      as
Fired,

103Btu/lb
                                   Human,
                                   Anatomical 
                                               8 - 12
                                                      50 - 75
                                                             70 - 90
                                                                      0.8 -
3.6
                                   Plastics 
                                   Swabs
                                   Adsorbents 
                                              14 - 20
                                                      5 - 144
                                                              0 - 1
                                                                      13.9
- 20
                                   Animal
                                   Infected
                                   Anatomical 
                                              11 - 14
                                                      5 - 62
                                                              0 - 30
                                                                      5.6 - 12
                                   Animal
                                   Infected
                                   Anatomical 
                                               9 - 16
                                                      48 - 62
                                                             0 - 0.2
                                                                       11 - 14
                                   Glass 
                                                0
                                                     175 - 225
                                                               0
                                                                        0
                                   Bedding,
                                   Shaving
                                   Paper, Fecal
                                   Matter 
                                               8 - 9
                                                      20 - 45
                                                             10 - 50
                                                                       4 - 8.1
                                   Gauze Pads,
                                   Swabs
                                   Garments,
                                   Paper
                                   Cellulose 
                                               8 - 12
                                                      5 - 62
                                                              0 - 30
                                                                      5.6 - 12
                                   Plastics,
                                   PVC,
                                   Syringes 
                                              9.7 - 20
                                                      5 - 144
                                                              0 - 1
                                                                      9.6 - 20
                                   Sharps,
                                   Needles 
                                                60
                                                     450 - 500
                                                              0 - 1
                                                                       0.06
                                   Fluids,
                                   Residuals 
                                               0 -10 
                                                      62 - 63
                                                             80 - 100
                                                                       0 - 8


                           Pathological wastes such as animal carcasses and
human body parts are
                           usually handled separately by burning on a batch
basis in a dedicated
                           incineration facility. Such waste has very high
moisture content and produces no
                           acid-gas emissions and particulate emissions are
relatively harmless oxides of
                           calcium. 

                           Gaseous Emission Control
                           Many types and sizes of air-pollution-control
equipment are on the market,
                           designed to clean gas streams of solid, liquid,
and gaseous pollutants. The most
                           common types are the fiber filter (bag house),
the wet scrubber, the dry
                           electrostatic precipitator (ESP), the wet
electrostatic precipitator (WESP), and
                           the CONDENSING WESP. 

                           The Nature of Pollutants
                           The primary requirement when selecting the best
gas-cleaning method is a sound
                           knowledge of the particulates to be
removed--principally, particle size distribution,
                           concentration, and chemical composition. 

                           The pollutants from incineration are a function
of many factors, including the
                           composition of the waste, charging rate, method
of charge, furnace type and
                           design, burn conditions (temperature,
turbulence, time), and excess air. 

                           Particulate matter (including heavy metals,
dioxins, furans, and mercury),
                           chlorides, and sulfur oxides are the most common
pollutants in the incinerator
                           gas stream requiring substantial removal. Other
pollutants, if present, often will be
                           removed by the same control arrangements. 

                           Particulate Type and Size
                           Particulate size is measured in microns
(micrometers). Particles are classified
                           according to their mode of formation as dust,
fumes, smoke, mists, or sprays. 

                           Dust, fumes, and smoke are solid particles. Dust
particles normally are larger
                           than one micron. Breaking up larger
particles--as by crushing or grinding--creates
                           smaller dust particles. 

                           Fumes are fine, solid particles formed by the
condensation of vapors of solid
                           materials, such as heavy metals and their
oxides. Fume particles normally are
                           smaller than one micron. 

                           Smoke comprises fine (less than one micron)
solid particles resulting from
                           incomplete combustion of organic materials. 

                           Mists and sprays are not products of
incineration but of the incinerator's
                           pollution-control equipment. Mists are liquid
droplets, generally smaller than 10
                           microns, generated in a gas scrubber. Sprays are
larger liquid droplets, ranging
                           from 10 to 400 microns. 

                           An aerosol is an assembly of small particles,
solid or liquid, suspended in a gas.
                           The diameter of the particles may vary from 100
microns down to 0.01 micron or
                           smaller. 

                           Particulate Concentration
                           The particulate concentration is a measure of
the total mass of all the particles
                           suspended in a given volume of gas. It is
usually measured as grains (gr) per
                           cubic ft (one lb = 7000 gr) or as grams per
cubic meter. 

                           Air-pollution-control systems are classified
according to the particulate
                           concentration of gas to be cleaned. For
hospital-waste incineration, total
                           particulate loading can be as high as 0.3 gr/scf. 

                           Particle-size Distribution
                           Particulate matter that originates in the
incinerator varies considerably in particle
                           size as well as concentration. Knowledge of
particle-size distribution therefore
                           can be important. The particle-size distribution
of a typical incineration sample is
                           illustrated in Table 2. 

                                                     Table 2A
                                Particulate Characteristics of a Typical
Incineration Sample --
                                                   Concentration

                                               LOCATION 1*
                                                               LOCATION 2**
                                   grains/dcf 
                                                    1.88
                                                                    0.01
                                   lbs/hr 
                                                   217.01
                                                                    1.48
                                   lbs/wet ton 
                                                   52.08
                                                                    0.36


                                                     Table 2B
                              Particulate Characteristics of a Typical
Incineration Sample -- Size
                                                    Distribution
                                        (Percent by Weight Less than
Indicated Size)

                                    Size, microns
                                               LOCATION 1* 
                                                              LOCATION 2** 
                                       18.7
                                                    37.9
                                                                   100.0
                                       11.7
                                                    30.6
                                                                    98.0
                                       8.0
                                                    16.4
                                                                    94.9
                                       5.4
                                                     6.6
                                                                    93.4
                                       3.5
                                                     2.6
                                                                    92.8
                                       1.8
                                                     1.6
                                                                    83.3
                                       1.1
                                                     0.9
                                                                    67.7
                                       0.76
                                                     0.1
                                                                    54.6



                            *Measured at incinerator outlet, w/out controls
burning 100 tons/day wet sludge
                                                      cake"
                              **Measured after venturi scrubber with a
total pressure drop of 30-in. wc.
                             Source: C.R. Brunner, Incineration ,Systems:
Selection and Design (New York: Van Nostrand
                                                   Reinhold, 1984).

                           Particle Settling Velocity
                           Particles suspended in relatively calm
atmosphere and regions of low gas velocity
                           surrender to gravity and slowly settle.
Gravitation causes a particle to move
                           downward at increasing velocity, but buoyancy
force and drag resist the
                           downward motion. The particle will fall at a
constant or settling velocity when the
                           gravitational force equals the combined buoyant
and drag forces. 

                           The smaller the particle, the less its response
to gravity and inertial forces. For
                           example, a 100-micron water droplet has a
settling velocity of 59.2 fpm, the
                           settling velocity of a 10-micron droplet is 059
fpm, for 1 micron, it's 0.007 fpm,
                           and for 0.1 micron, it is 0.00007 fpm. In other
words, fine and extremely fine
                           particles essentially never settle by gravity. 



                           About the author: Isaac Ray is a vice president
with Croll-Reynolds Clean Air
                           Technologies, 751 Central Avenue, PO Westfield,
NJ 07091-0668. Tel:
                           908-232-4200; Fax: 908-232-2146. 

--